Control Valve Flow
Continuous process industries, DCS questions. topic
Posted by Manpreet on 28 July, 2012 - 1:23 am
According to PCV installed here its datasheets show a range value of min to max flow with correspnding vlaue of precentage valve opening. So, there would not be any flow through PCV when The min valve position and corresponding flow is there. e.g. Min Flow in 70TPH and % valve Opening is 26%. When PCV is less than 26% then there would not be any flow?


Posted by otised on 28 July, 2012 - 1:42 pm
It means you should not operate the valve at less than 26% open. There will be flow when the valve is between 0 and 26% open, but the valve trim may not last very long if you operate there. You didn't say what the fluid is, but if it is liquid you may get cavitation or flashing. Your control system should be set up to force the valve closed when demand would call for position less than 26% open.


Posted by Mustafa R. on 30 July, 2012 - 3:32 am
Hi,

Shutdown that system had exposed is a type of alarm, don't worry it's good feature.

Best Regards
Mustafa R. Ahmed
Control and System Eng.
mustafariyadh89@yahoo.com

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
"He's the kind of man for the times that need the kind of man he is ..."
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive