Posted by MAZEN on 28 July, 2012 - 7:02 am
Is the flame detector (type of infrared detector) is affected by high temperature?


Posted by David on 29 July, 2012 - 10:49 pm
Yes.

Typical commercial flame detectors use lead sulfide (PbS). The photo sensitivity and dark resistance of PbS changes as the element temperature changes requiring temp compensation, but even temp comp is typically limited to 50°C (125°F) at an upper limit.

Recommended installation practices include ambient temperature limitations and detector protection from refractory heat which, without flicker analysis, PbS can not distinguish from flame IR energy.


Posted by Mustafa R. on 30 July, 2012 - 3:44 am
Dear Mazen,

Any electrical device will effect by high temperature, here you must choice the suitable flame detector for the plant or field that you want to setup it there. Some kind of flame detectors are X-Series which provided by DET-Tronics, one kind of this family stand with high temperature is "C7050/UVHT Flame Detector". For more details visit page add. below

www.detronics.com

Best Regards
Mustafa R. Ahmed
Control and System Eng.
mustafariyadh89@yahoo.com

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
Meskimen's Law:
There's never time to do it right, but there's always time to
do it over.
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive