Hi,
I have a problem with communication between PLC module 750-653 WAGO for serial MODBUS communication and Seneca ZSG module for weight measurement.
I try to get data from Seneca via MODBUS RTU interface on the back of the Seneca module, but module nothing sends to my PLC. I build a function block for serial communication and BUSMASTER_RTU block for serial communication. On Error code output i get error code 5. I can't find what 5 is stands for.
Thank You very much in advance
I have a problem with communication between PLC module 750-653 WAGO for serial MODBUS communication and Seneca ZSG module for weight measurement.
I try to get data from Seneca via MODBUS RTU interface on the back of the Seneca module, but module nothing sends to my PLC. I build a function block for serial communication and BUSMASTER_RTU block for serial communication. On Error code output i get error code 5. I can't find what 5 is stands for.
Thank You very much in advance
![]() ![]() |
I have no idea what error code 5 is, but here's a list of things that can go wrong with serial communications:
- slave module address (DIP switch on ZSG, configured on the Wago end)
- baud rate same on both ends (DIP switch on ZSG)
- parity has to be the same on both ends
- RTU is 8 data bits, not 7
- on RS-485, different vendors define the RS-485 A and B lines the opposite from other vendors. Having the A and B lines backwards doesn't damage RS-485 drivers, but the signal/data won't get through. Try swapping A/B lines on one end.
It isn't crystal clear from the spec sheet whether the RS-232 port is capable of Modbus RTU. The RS-485 port is definitely Modbus enabled, mentioned on page 1 and shown in the application example diagram on page 2. The same app diagram shows the RS-232 port connected to a PC labeled "(setting)", which I interpret as "configuration". The RS-232 port might be for configuration only. Only a manual will tell for sure, or maybe not, given the state of documentation, in general. I'd be inclined to work with the RS-485 port for Modbus.
- slave module address (DIP switch on ZSG, configured on the Wago end)
- baud rate same on both ends (DIP switch on ZSG)
- parity has to be the same on both ends
- RTU is 8 data bits, not 7
- on RS-485, different vendors define the RS-485 A and B lines the opposite from other vendors. Having the A and B lines backwards doesn't damage RS-485 drivers, but the signal/data won't get through. Try swapping A/B lines on one end.
It isn't crystal clear from the spec sheet whether the RS-232 port is capable of Modbus RTU. The RS-485 port is definitely Modbus enabled, mentioned on page 1 and shown in the application example diagram on page 2. The same app diagram shows the RS-232 port connected to a PC labeled "(setting)", which I interpret as "configuration". The RS-232 port might be for configuration only. Only a manual will tell for sure, or maybe not, given the state of documentation, in general. I'd be inclined to work with the RS-485 port for Modbus.
![]() ![]() |
Thank You for helping. I think that I made all above and still I don't get signals from ZSG. Can be problem with data structure and receiving 16 bit register from ZSG to 8 bit variable in receiving data variables?
And I think that maybe I didn't put terminal resistor on both ends? On 750-653 and on ZSG side?
And I think that maybe I didn't put terminal resistor on both ends? On 750-653 and on ZSG side?
![]() ![]() |
The error is MB_ILLEGAL_NUMBER_OF_POINTS. You can check this from the /library manager/data types in codesys.
![]() ![]() |
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.