Communications systems and equipment. topic
Posted by Marty on 11 August, 2012 - 3:09 pm
Have trouble getting modbus comms from a Omni Flow Computer 6000 through a Modicon multiplexer BM85 to a Modicon Quantum PLC with Modbus Plus on the PLC. Already have modbus data coming from a Allen Bradley PLC and HMI to the Modicon with no troubles. These are slave devices though and i need to be a master. I can talk to the Modicon PLC through the Multiplexer to do any programming to the PLC. Any ideas?


Posted by Mark on 12 August, 2012 - 12:27 am
Hello,

Read the Omni flow MODBUS documents. I am not being flippant.

Omni flow computers can support standard MODBUS but really are ENRON MODBUS.

You must be sure to read the correct registers and have the flow computer set up correctly.

Good luck,

Mark
http://www.peakhmi.com/


Posted by Lynn August Linse on 14 August, 2012 - 9:01 am
Mark is correct - the Omni flow has a mode which I believe they call 'Modicon Compatibility Mode' which defaults off, but allows most (all?) Modicon devices to talk to the Omni Flow, so the BM85 should work.

Also, you may need to avoid the magic-sized, user-configured region of the Omni register map where you poll say 100 registers but might only get 6 bytes back (or even 0 bytes). Few Modbus masters support such unpredictable response sizes.


Posted by Richard on 13 August, 2012 - 4:18 pm
Hi,

FieldServer using their gateway can convert Modbus Omniflow to Modbus RTU, have a look at www.fieldserver.com

Thanks,

Richard

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
Anyone who goes to a psychiatrist ought to have his head examined.
-- Samuel Goldwyn
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive