NEMA 7 cabinet purge: air or nitrogen?
Engineering and workplace issues. topic
Posted by FingerLaker on 23 August, 2012 - 9:22 am
So if you have a control panel in a NEMA 7 cabinet with an explosion proof classification, how would you choose between the option of an air purge or nitrogen purge for a purge system? Is it the availability of compressed N2 or any other consideration? Thanks.


1 out of 2 members thought this post was helpful...
Posted by Bob Peterson on 23 August, 2012 - 12:36 pm
why would you purge a NEMA7 enclosure in the first place?

--
Bob


Posted by FingerLaker on 20 September, 2012 - 3:01 pm
I'm sorry, you are right. No point in purging an explosion proof enclosure. For purging a NEMA 4, what is the reason to use air or nitrogen. Thanks.

> why would you purge a NEMA7 enclosure in the first place?


Posted by Ray Zimbal - MD&G+Controls on 21 September, 2012 - 8:34 am
>For purging a NEMA 4, what is the reason to use air or nitrogen.

You need to be sure of utilize a purge rated NEMA enclosure, so that you have adequate sealing to control Nitrogen loss.


Posted by Roy Matson on 23 September, 2012 - 6:10 am
I think it would first of all be determined by what your source is i.e. you wouldn't purge with Nitrogen from bottles, but if you had a waste stream of dry Nitrogen 24/7, you might. otherwise air is the most common.

Another consideration is the panels location. if it's indoors, Nitrogen could present a safety hazard by displacing all the air.

I should add I have never seen anything but air used.

Roy


Posted by David Todd on 24 September, 2012 - 5:39 am
I would use air for purging as a matter of safety for maintenance personnel. I don't know how big your panel is but if it is opened by maintenance people and they are not aware they could breath in nitrogen from a nitrogen purged panel and be overcome by lack of oxygen.


Posted by S Venkataramanan on 24 September, 2012 - 10:07 am
I agree with the statement that air is more safe. If we have to do maintenance in such panel then we must ensure that the panel is purged with air several times to achieve the oxygen level needed. That means long downtime.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
Food for thought is no substitute for the real thing.
-- Walt Kelly, "Putluck Pogo"
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive