Can anyone explain the relationship between Profibus DP/PA, Hart and ASI bus systems.
Also need to understand instead of using profibus PA. what is recommended so that I can measure 4-20ma output signal on the field?
Also need to understand instead of using profibus PA. what is recommended so that I can measure 4-20ma output signal on the field?
![]() ![]() |
There are some differences in the communication protocol capabilities, and therefore
- PROFIBUS-DP primarily used with variable speed drives and motor starters
- PROFIBUS-PA, HART, and FOUNDATION fieldbus primarily used with transmitters, analyzers, and valve positioners
- ASI primarily used with on/off switches and actuators
- HART digital communication is slow and is not used for closed loop control. Closed loop control is done using analog 4-20 mA
- FOUNDATION fieldbus is suitable for closed loop digital control using cyclic digital real-time data on a time-synchronized and scheduled, precisely periodic macrocycle
- ASI only communicates cyclic I/O, no acyclic diagnostics or setup
- PROFIBUS-DP/PA, HART, and FOUNDATION fieldbus support acyclic data for intelligent device setup and diagnostics
- PROFIBUS-DP/PA, HART, and FOUNDATION fieldbus support EDDL (www.eddl.org) for intelligent device management
- PROFIBUS-PA, HART, and FOUNDATION fieldbus are intrinsically safe and long distance, suitable for use in the process industries
- ASI is not intrinsically safe, and not long distance, but is very fast
See the guide on Institutionalizing Device Diagnostics here for a cross-reference table of protocols and devices:
http://www.eddl.org/DeviceManagement/Pages/DeviceDiagnostics.aspx
The principal beauty of PROFIBUS-PA and FOUNDATION fieldbus H1 is that you can do away with analog 4-20 mA and the associated drawbacks. Use either native PA or H1 devices, this way you eliminate 4-20 mA completely.
Or are you saying that you need some device not available in a PA or H1 version? What device is that? For Fieldbus you can see available devices here:
http://www.fieldbus.org/index.php?option=com_mtree&Itemid=324
If a native device is really not available, then use a converter device which has a PA or H1 connection, and 4-20 mA input/output as needed. See the Fieldbus Foundation website:
http://www.fieldbus.org/index.php?option=com_mtree&task=search& amp;Itemid=324&ffbstatus=Registered&ffbmfg=&ffbcategory=Conve rter+%28Transducer%29
Cheers,
Jonas
moderator's note: these are long URLs; please remove any spaces the forum software inserts
- PROFIBUS-DP primarily used with variable speed drives and motor starters
- PROFIBUS-PA, HART, and FOUNDATION fieldbus primarily used with transmitters, analyzers, and valve positioners
- ASI primarily used with on/off switches and actuators
- HART digital communication is slow and is not used for closed loop control. Closed loop control is done using analog 4-20 mA
- FOUNDATION fieldbus is suitable for closed loop digital control using cyclic digital real-time data on a time-synchronized and scheduled, precisely periodic macrocycle
- ASI only communicates cyclic I/O, no acyclic diagnostics or setup
- PROFIBUS-DP/PA, HART, and FOUNDATION fieldbus support acyclic data for intelligent device setup and diagnostics
- PROFIBUS-DP/PA, HART, and FOUNDATION fieldbus support EDDL (www.eddl.org) for intelligent device management
- PROFIBUS-PA, HART, and FOUNDATION fieldbus are intrinsically safe and long distance, suitable for use in the process industries
- ASI is not intrinsically safe, and not long distance, but is very fast
See the guide on Institutionalizing Device Diagnostics here for a cross-reference table of protocols and devices:
http://www.eddl.org/DeviceManagement/Pages/DeviceDiagnostics.aspx
The principal beauty of PROFIBUS-PA and FOUNDATION fieldbus H1 is that you can do away with analog 4-20 mA and the associated drawbacks. Use either native PA or H1 devices, this way you eliminate 4-20 mA completely.
Or are you saying that you need some device not available in a PA or H1 version? What device is that? For Fieldbus you can see available devices here:
http://www.fieldbus.org/index.php?option=com_mtree&Itemid=324
If a native device is really not available, then use a converter device which has a PA or H1 connection, and 4-20 mA input/output as needed. See the Fieldbus Foundation website:
http://www.fieldbus.org/index.php?option=com_mtree&task=search& amp;Itemid=324&ffbstatus=Registered&ffbmfg=&ffbcategory=Conve rter+%28Transducer%29
Cheers,
Jonas
moderator's note: these are long URLs; please remove any spaces the forum software inserts
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.
Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.
Fortune
Conceit causes more conversation than wit.
-- LaRouchefoucauld








on 30 August, 2012 - 10:13 am