Posted by zedd on 11 September, 2012 - 11:30 am
Hi!

I discussed with my friend today about wiring a switch to a digital input. The discussion was about the zero in the case in the picture (see link). Is this a proper wiring or do I have to wire the zero to the input-card? We both know there is more simple solutions but we couldn't agree about this example.

http://i.imgur.com/rpcSB.jpg


Posted by Roy Matson on 11 September, 2012 - 2:43 pm
Yes, wire the -24 Volt to the card also. even if it's somehow connected through the ground system, it should be connected directly to negative to be correct.

Roy


Posted by Bruce Axtell on 12 September, 2012 - 2:09 am
Yes, you would need to bring back what you call zero.

However, just because you CAN do it, doesn't mean you SHOULD do it.

Generally, it is not a good practice to mix voltages from different sources.

It would be preferable to use an isolation relay on the field side and wire the dry contact of the relay to switch the voltage of the PLC panel.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
... bleakness ... desolation ... plastic forks ...
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive