Error value during transmitter calibration
Sensor technologies. topic
Posted by sanjib on 26 September, 2012 - 11:57 pm
We have pressure transmitter of following specification:

1) Make : ABB; Model: 264HS
2) Span: 24-2400 KPa
3) Accuracy: 0.075 % Span:
4) Calibration Range: 0-4 Kg/cm2

During calibration how much error value can we consider? What is the allowable error? Please tell


Posted by Roy Matson on 28 September, 2012 - 2:04 pm
>During calibration how much error value
>can we consider? What is the allowable
>error? Please tell

That's entirely up to you
Your calibration is only 16% of the transmitters span, if you need better acuracy you should have purchased range M 600 kPa.

If you don't need super accuracy I'm sure it will be fine.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.