from the Forum department...
Frame V Turbine Compartment temperature Setting
Posted by DNA on 29 September, 2012 - 8:11 am
Looking for standard setting for 26QA-1 on John Brown Frame V Turbine.
DNA
Posted by MIKEVI on 29 September, 2012 - 9:23 am
Dear DNA, I am not sure exactly which switch you are looking for a setting on. The title of your post says turbine comp't temperature setting, but then another part of the post lists 26BA-1, and lastly in your post it lists 26QA-1, so I'm a bit confused.
A device spec I have for a vintage 1985 Frame 5001P has the following settings, hopefully one of them is what you are really looking for. I do not have a listing for 26BA-1, seems like some sort of alarm setpoint.
26BT-1, turbine comp't high temp alarm 300 degf.
26BT-2, turbine comp't fan shutoff 95 degf.
26HT-1 Turbine comp't heater control 40degf.
Lastly 26QA-1 lube oil header temp high alarm 165 degf. which of course has nothing to do with the turbine comp't temperature.
I hope one of these is what you needed and it seems realistic for your machine.
Posted by DNA on 29 September, 2012 - 10:57 am
MIKEVI, thanks for the quick response, the figures you have given look good, the QA was a typing error when reading from device list.
Cheers
DNA
Posted by MIKEVI on 1 October, 2012 - 4:35 pm
Dear DNA, no worries, glad to be of help.
A nuclear war can ruin your whole day.
Advertise here
Advertisement
our advertisers