Dear All,
I am using Invensys Eurotherm PAC T2550 with wonderware and using Eurotherm suite.
i have created one sequential logic, in which i have created few steps. Now my question is, is it possible to know current running step of my sequence in scada / wonderware ?
Thanks in advance.
Bhargav.
I am using Invensys Eurotherm PAC T2550 with wonderware and using Eurotherm suite.
i have created one sequential logic, in which i have created few steps. Now my question is, is it possible to know current running step of my sequence in scada / wonderware ?
Thanks in advance.
Bhargav.
![]() ![]() |
A look at a spec sheet shows that comm protocols are options, so presuming you want to use Modbus you need to check to make sure you have the option code for Modbus (spec sheet shows order codes for updating options). The T2550 can operate as a Modbus slave or a Modbus master.
A look at the T2550 manual HA 028 898 shows a short section on Modbus, which seems integrated into what Eurotherm calls LIN, a Local Instrument Network. The T2550 manual refers to a Modbus Tools Help document (Part no. HA028988). (I found version 5, Sept 2011).
In the Modbus Tools Help, page 13 shows a screen shot of an editing function, where several data parameters are identified as pid1.PV, pid2.PV, pid1.FALLBACK. That appears to be internal tags identifying various parameters in the controller.
It appears that if the sequential logic stages are tagged, (enabled/disabled, numbered, named, whatever) then the T2550 can place the respective tag(s) in Modbus register(s).
A look at the T2550 manual HA 028 898 shows a short section on Modbus, which seems integrated into what Eurotherm calls LIN, a Local Instrument Network. The T2550 manual refers to a Modbus Tools Help document (Part no. HA028988). (I found version 5, Sept 2011).
In the Modbus Tools Help, page 13 shows a screen shot of an editing function, where several data parameters are identified as pid1.PV, pid2.PV, pid1.FALLBACK. That appears to be internal tags identifying various parameters in the controller.
It appears that if the sequential logic stages are tagged, (enabled/disabled, numbered, named, whatever) then the T2550 can place the respective tag(s) in Modbus register(s).
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.
Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.
Fortune
If you eat a live frog in the morning, nothing worse will happen to
either of you for the rest of the day.







on 6 October, 2012 - 12:39 am
on 6 October, 2012 - 9:33 am