Posted by Tariq on 7 October, 2012 - 11:54 am
We have three phase two UPS of 30KVA each in parallel operation. From the last four months inverter fails problem arises in each of UPS. We checked our system thoroughly and finds out nothing. But we checked our output currents and finds out that neutral current (5.7 Amp) is higher than individual currents (4.7 Amp). Our system output neutral is not grounded and it is in floating condition.

Requires technical comments to resolve this issue.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.