Hello,
A customer has a few Modicon Remote-I/O modules of type J890, and we are not fully sure how to set a J890 to the corresponding drop number on the RIO network. The drop number is set via a DIP switch. We guess that the number is to be set binarily. That means, e.g., flipping up first and third switch lever makes a value of 5. Should - in addition - a 1 be added to the binary value (making 1 and 3 up rather 6 than 5)?
A customer has a few Modicon Remote-I/O modules of type J890, and we are not fully sure how to set a J890 to the corresponding drop number on the RIO network. The drop number is set via a DIP switch. We guess that the number is to be set binarily. That means, e.g., flipping up first and third switch lever makes a value of 5. Should - in addition - a 1 be added to the binary value (making 1 and 3 up rather 6 than 5)?
![]() ![]() |
From what I could find, the sws for addressing set the addressing starting at "1" with all switches OFF (original Modicon addressing always started at "1", "0" was not a valid starting address).
Address switchpack only uses sws 1 -5 (6/7/8 not used). Other switchpack is for ASCII settings.
All sws off = 1, all sws on = 32
Address switchpack only uses sws 1 -5 (6/7/8 not used). Other switchpack is for ASCII settings.
All sws off = 1, all sws on = 32
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.