Hi
Is it possible to connect all channels of the allen bradley 1756-IF16 with analog input via intrinsic safe isolator like MTL 5041? All of my signals are intrinsic safe and I have isolators (not barriers) installed inside the PLC cabinet. I have to wire the analog signal from the isolator to 1756-IF16.
The wiring drawing of the card 1756-IF16 doesn't show the 4 wire transmitter connection (isolators are sourcing the 4-20mA). The wiring says the card is single ended (i think it means non-isolated).
So will it be possible to connect the current (4-20mA) signal from intrinsic safe isolator to 1756-IF16, if yes please explain how.
Thanks
Is it possible to connect all channels of the allen bradley 1756-IF16 with analog input via intrinsic safe isolator like MTL 5041? All of my signals are intrinsic safe and I have isolators (not barriers) installed inside the PLC cabinet. I have to wire the analog signal from the isolator to 1756-IF16.
The wiring drawing of the card 1756-IF16 doesn't show the 4 wire transmitter connection (isolators are sourcing the 4-20mA). The wiring says the card is single ended (i think it means non-isolated).
So will it be possible to connect the current (4-20mA) signal from intrinsic safe isolator to 1756-IF16, if yes please explain how.
Thanks
![]() ![]() |
You can use a 4-wire device with the IF16 card, but you will be limited to 8 devices per card (a 4-wire device [differential] uses two inputs).
see: http://literature.rockwellautomation.com/idc/groups/literature/documen ts/um/1756-um009_-en-p.pdf
Page 70
see: http://literature.rockwellautomation.com/idc/groups/literature/documen ts/um/1756-um009_-en-p.pdf
Page 70
![]() ![]() |
Hi Kevin
Thanks for the reply. I shouldn't have said 4 wire. all of my transmitters are 2 wire, powered by the intrinsic safe isolator. So basically the loops behave like 4 wire but not 4 wire and the analog signal from the isolator (sourcing from the isolator) to be connected to IF16.
All of the isolators and PLC powered from the same 24VDC power supply. Is there going to be any issue.
Thanks for the reply. I shouldn't have said 4 wire. all of my transmitters are 2 wire, powered by the intrinsic safe isolator. So basically the loops behave like 4 wire but not 4 wire and the analog signal from the isolator (sourcing from the isolator) to be connected to IF16.
All of the isolators and PLC powered from the same 24VDC power supply. Is there going to be any issue.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.
Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.
Fortune
Important letters which contain no errors will develop errors in the
mail. Corresponding errors will show up in the duplicate while the
Boss is reading it.







on 14 October, 2012 - 12:16 pm