from the E & I department...
single 2-wire Tx for PLC and DCS
Posted by Instrument on 17 October, 2012 - 8:48 pm
We are using siemans PLC and yokogawa DCS. I want to connect a single 2-wire level transmitter for both DCS & PLC. Already we connected this transmitter to PLC and working well. and we need same transmitter indication at DCS? PLZ Suggest how to connect?
Posted by Russ B on 18 October, 2012 - 8:10 am
What protocol is on these 2 wires?
4-20mA, 0-10 VDC, Modbus RTU?
Posted by Roy Matson on 20 October, 2012 - 1:11 am
If both your DCS and PLC are close together all you have to do is wire to the 4-20 mA input of 1 then take a pair of wires from across the conditioning resistor and run them to a 1-5V input of the other.
Another method is to use a signal isolator in series with the 4-20 mA loop and connect it to the 4-20mA input of the other system
Easy Peasy
Posted by Roy Matson on 20 October, 2012 - 1:15 am
By the way
The signal isolator method is how you connect 1 transmitter to a safety shutdown system, the shutdown system gets the primary signal and the other system gets the re-transmitted signal
Roy