Induction Generator online from runaway speed
Power generation equipment control. topic
Posted by hydro on 18 October, 2012 - 10:51 pm
I have a 20kW induction motor running as a generator. The prime mover would be supplying approximately 5kW of power with the generator off line at runaway speed (~1.8 x rated). If I then put the generator on line, would the the torque and current be similar to DOL as a motor, with torque in opposite direction?


Posted by Phil Corso on 20 October, 2012 - 10:18 pm
Hydro...

1) If operated off-line as an induction-generator, what is the size of the capacitor connected to the motor's terminals?

2) DO NOT connect the motor to the line while running it at such a high rate of speed!

Regards, Phil Corso


Posted by hydro on 22 October, 2012 - 7:33 pm
When off-line, it would not be generating, there would be no load or capacitor connected.

I am looking for a way to bring the unit online without mechanically throttling the speed. Maybe a regenerative VFD? however I was hoping to keep it simpler than that.


Posted by Phil Corso on 23 October, 2012 - 10:32 am
Hydro... what does "5 kW, off-line at runaway speed (~ 1.8 x rated)" represent?

Phil


Posted by Phil Corso on 23 October, 2012 - 2:18 pm
Hydro... further to my earlier post:

Runaway speed can be far greater than your IG's nominal speed rating. And, it is expected when there is a sudden loss of the connection between the IG and its network!

However, sudden connection of the IG to its network should never be done if the IG is rotating much faster than it would at nominal output.

For example, let's say you have a 2-pole motor, rated 2,850 rpm when connected to a 50 Hz supply. Its rated slip is then 100x[(3,000-2,850)/3,000} or 5%. Then its speed as an IG should be around 5% above 3,000 or 3,150rpm!

However, if its speed when connected to the network is much greater than 5%, it will act as a brake... resulting in a snapped shaft or much worse... torn off its foundation!

Phil


Posted by hydro on 24 October, 2012 - 9:29 pm
Thanks Phil,

I understand that there is going to be high torque, but as it is quite usual to start a 5kW motor from standstill (DOL). I am trying to understand if this breaking torque is any worse than DOL torque.


Posted by Phil Corso on 25 October, 2012 - 1:38 am
Hydro... consider the induction motor used in the example above! Its rated sub-synchronous speed as a motor is 2,850 rpm, while as a generator its hyper-synchronous speed is 3,150 rpm.

Its speed-torque curve operated as a motor, suitable for DOL-Starting, is similar to its torque-speed-curve as an induction-generator! For motor-action 'slip' is positive while for generator-action, 'slip' is negative.

The motor's rotor experiences a reverse torque as its speed transitions from sub-synchronous to hyper-synchronous-speed. Rated electrical power-output is reached when speed is about 5% above line-frequency. As speed increases beyond that, electrical power-output continues to increase until pull-out torque is reached! Then power-output will decrease! So, you are correct that the stress is similar to that experienced for DOL-starting!

Now consider the situation you described... what happens if an non-excited machine is suddenly connected to the network at a runaway speed, that is, say double rated speed? The above paragraph stated that the torque-speed curves are 'similar', but there is a notable difference.

Maximum torque varies with 'slip'! And slip is positive for sub-synchronous, but negative for hyper-synchronous speeds. Thus, pull-out torque magnitude is greater for hyper-synchronous speed. This characteristic 'could' severely damage the machine!

Please note, I said 'could' because whether or not the machine will experience damage is very, very, dependent on its electrical parameters! In other words, it is machine-specific

Regards, Phil


1 out of 1 members thought this post was helpful...
Posted by Phil Corso on 25 October, 2012 - 7:44 am
Hydro... the influence a motor's parameters has on its generator-action torque can be seen in the following thread:

http://www.control.com/thread/1026155353

The thread covers derivation of a motor's maximum torque, Tm, when operating sub-synchronously!

Note the denominator for Tmax. The last term, R1, is positive for sub-synchronous operation. For hyper-synchronous operation that term becomes negative, resulting in a higher (than design) Tmax!

Now you can see why Tmax is motor-specific.

Phil


1 out of 1 members thought this post was helpful...
Posted by hydro on 25 October, 2012 - 9:51 pm
Thanks Phil,

Most speed-torque curves I have seen show the curve mirrored/inverted about the synchronous speed/0 torque axes.

Are you saying that that is not totally correct, that the R1 term makes the magnitude on the generator side of the curve slightly larger? And since R1 is machine specific, the difference in magnitude is also machine specific?


1 out of 1 members thought this post was helpful...
Posted by Phil Corso on 26 October, 2012 - 12:03 am
Hydro... in a nutshell, yes!

I want to clarify my statement that "... stress is similar to that experienced for DOL-Starting!"

At starting a motor produces a starting-torque (also called locked-rotor or breakaway) which is about 150% of its full-load or rated-torque. As motor speed increases the torque reaches a maximum value of 200-250%, called its pullout or breakdown-torque. Then, torque decreases until it reaches full-load torque at design slip.

You have noted that for hyper-synchronous operation torque is negative. And, its generator-action value occurs long before the pullout magnitude is reached. That value, because of the R1 being negative, can be 300-400% of full-load value!

Phil

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
"I'd love to go out with you, but I've been scheduled for a karma
transplant."
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive