Hi experts
Is barrier required for simple apparatus like RTD, LAMPS, PB etc.
RTD, PB, LAMPS located in Hazardous area.
Thank in advance.
Bond
Is barrier required for simple apparatus like RTD, LAMPS, PB etc.
RTD, PB, LAMPS located in Hazardous area.
Thank in advance.
Bond
![]() ![]() |
Simple answer - yes.
A simple device, by definition, is one that cannot generate more than 1.5 V, 100 mA, or 25 mW, or has energy-storing components with well-defined parameters. So the energy that the simple device can supply to the circuit is limited. However, the energy that can be supplied by the external circuits connected to the component are not restricted in any way - so an energy-limiting component (barrier or isolator) is needed between the IS part of the circuit and the rest of he world.
A simple device, by definition, is one that cannot generate more than 1.5 V, 100 mA, or 25 mW, or has energy-storing components with well-defined parameters. So the energy that the simple device can supply to the circuit is limited. However, the energy that can be supplied by the external circuits connected to the component are not restricted in any way - so an energy-limiting component (barrier or isolator) is needed between the IS part of the circuit and the rest of he world.
![]() ![]() |
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.
Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.
Fortune
Children are natural mimic who act like their parents despite every
effort to teach them good manners.








on 19 October, 2012 - 3:16 pm