What is the advantage enabling Inlet Guide Vane temperature control in combined cycle operation? how is heat input to the boiler increased at lower gas turbine loads during start-up in combined cycle operation?
![]() ![]() |
> What is the advantage enabling Inlet Guide Vane temperature control in combined cycle operation?
I am talking about Frame7E(mark VIe). Consider IGV Temp control OFF. During startup, IGV opens to keep exhaust temp ref to about 700(*F). Till GT reaches 40 MW,IGV is about 57 degree open (from FSNL to 40 MW). As load increases temp reference goes up and IGV start opening more to admit more inlet air to keep temp ref is about 700 and at base load IGV is full open (84) and temp ref is never 700 but about 1000. So this additional air is diluting the heat for HRSG. In opposite action when IGV temp control is ON this excess air is not required to cool the temp ref to 700 so air intake is minimised and net heat gain is far more then the case if it were IGV TEMP CONTROL is OFF. So this heat is utilized in HRSG to make more steam. One more thing at base load IGV TEMP CONTROL should be OFF. I hope CSA or other experts will give more detail about this. Waiting for their inputs.
Thanks
I am talking about Frame7E(mark VIe). Consider IGV Temp control OFF. During startup, IGV opens to keep exhaust temp ref to about 700(*F). Till GT reaches 40 MW,IGV is about 57 degree open (from FSNL to 40 MW). As load increases temp reference goes up and IGV start opening more to admit more inlet air to keep temp ref is about 700 and at base load IGV is full open (84) and temp ref is never 700 but about 1000. So this additional air is diluting the heat for HRSG. In opposite action when IGV temp control is ON this excess air is not required to cool the temp ref to 700 so air intake is minimised and net heat gain is far more then the case if it were IGV TEMP CONTROL is OFF. So this heat is utilized in HRSG to make more steam. One more thing at base load IGV TEMP CONTROL should be OFF. I hope CSA or other experts will give more detail about this. Waiting for their inputs.
Thanks
![]() ![]() |
sardar9,
This is just to clarify your post. For units with conventional combustors (such as yours) and the ability to select IGV Exhaust Temperature Control (sometimes simply called IGV Temperature Control) ON and OFF, when it's selected OFF and the unit is loaded from initial breaker closure, the the IGVs will remain at minimum (usually 57 DGA for a Frame 7EA) until the exhaust temperature reaches 700 deg F. At this point as load is increased (fuel flow is increased) the IGVs will open to maintain 700 deg F until finally the IGVs are fully open. So, the IGVs will "modulate" to hold 700 deg F from minimum operating angle to maximum operating angle.
When the IGVs are fully open (usually 84 DGA for your units), as load (and fuel flow ) are increased the exhaust temperature will increase until it reaches the CPD-biased Exhaust Temperature Control Reference (TTRX) at which time the unit will be on CPD-biased Exhaust Temperature Control, affectionately referred to as "Base Load."
When IGV Exhaust Temperature Control is selected ON when the unit is being loaded from initial breaker closure, the IGVs will remain at minimum operating angle as the unit is loaded (as fuel flow-rate) is increased until the exhaust temperature gets to within approximately 10 deg F of the CPD-biased Exhaust Temperature Control Reference (TTRX). At that point as load (and fuel flow) is increased the IGVs will open to keep the exhaust temperature very close to TTRX until the IGVs reach maximum operating angle (again, usually 84 DGA for units like yours), and at that point the unit is at or very near Base Load and it will not be possible to increase the load (or exhaust temperature) by very much, if at all.
By holding the IGVs at minimum during loading when IGV Exhaust Temperature Control is selected ON, the exhaust temperature is "maximized" which increases steam production if the gas turbine exhaust is being used in a HRSG (Heat Recovery Steam Generator), or "boiler" at loads less then Base Load. Because, with IGV Exhaust Temperature Control selected OFF, the exhaust temperature is much less than maximum during loading from low load to Base Load.
Reducing the IGV angle during loading does increase (maximize) exhaust temperature during low loads, but it also decreases the heat rate of the gas turbine--meaning that the gas turbine is less efficient. However, the increased steam production causes the overall plant heat rate to rise because of the increases steam production, so it's a good trade-off.
If the unit does NOT have an HRSG (boiler) on the exhaust, or if the exhaust is not being directed through a damper to an HRSG (boiler) then it's NOT recommended to select IGV Exhaust Temperature Control ON, as it reduces the efficiency of the gas turbine.
By the way, the reason the IGVs are modulated when IGV Exhaust Temperature Control is selected OFF on units with conventional combustors is that it is found to reduce combustor dynamics at the load range where the IGVs are modulated, thereby improving hot gas path parts life (combustion liners; combustion transition pieces; cross-fire tubes and clips; etc.).
This is just to clarify your post. For units with conventional combustors (such as yours) and the ability to select IGV Exhaust Temperature Control (sometimes simply called IGV Temperature Control) ON and OFF, when it's selected OFF and the unit is loaded from initial breaker closure, the the IGVs will remain at minimum (usually 57 DGA for a Frame 7EA) until the exhaust temperature reaches 700 deg F. At this point as load is increased (fuel flow is increased) the IGVs will open to maintain 700 deg F until finally the IGVs are fully open. So, the IGVs will "modulate" to hold 700 deg F from minimum operating angle to maximum operating angle.
When the IGVs are fully open (usually 84 DGA for your units), as load (and fuel flow ) are increased the exhaust temperature will increase until it reaches the CPD-biased Exhaust Temperature Control Reference (TTRX) at which time the unit will be on CPD-biased Exhaust Temperature Control, affectionately referred to as "Base Load."
When IGV Exhaust Temperature Control is selected ON when the unit is being loaded from initial breaker closure, the IGVs will remain at minimum operating angle as the unit is loaded (as fuel flow-rate) is increased until the exhaust temperature gets to within approximately 10 deg F of the CPD-biased Exhaust Temperature Control Reference (TTRX). At that point as load (and fuel flow) is increased the IGVs will open to keep the exhaust temperature very close to TTRX until the IGVs reach maximum operating angle (again, usually 84 DGA for units like yours), and at that point the unit is at or very near Base Load and it will not be possible to increase the load (or exhaust temperature) by very much, if at all.
By holding the IGVs at minimum during loading when IGV Exhaust Temperature Control is selected ON, the exhaust temperature is "maximized" which increases steam production if the gas turbine exhaust is being used in a HRSG (Heat Recovery Steam Generator), or "boiler" at loads less then Base Load. Because, with IGV Exhaust Temperature Control selected OFF, the exhaust temperature is much less than maximum during loading from low load to Base Load.
Reducing the IGV angle during loading does increase (maximize) exhaust temperature during low loads, but it also decreases the heat rate of the gas turbine--meaning that the gas turbine is less efficient. However, the increased steam production causes the overall plant heat rate to rise because of the increases steam production, so it's a good trade-off.
If the unit does NOT have an HRSG (boiler) on the exhaust, or if the exhaust is not being directed through a damper to an HRSG (boiler) then it's NOT recommended to select IGV Exhaust Temperature Control ON, as it reduces the efficiency of the gas turbine.
By the way, the reason the IGVs are modulated when IGV Exhaust Temperature Control is selected OFF on units with conventional combustors is that it is found to reduce combustor dynamics at the load range where the IGVs are modulated, thereby improving hot gas path parts life (combustion liners; combustion transition pieces; cross-fire tubes and clips; etc.).
![]() ![]() |
Well explain CSA, I am still confuse about the inverted slop of exhaust temp Vs CPD/FSR bias. Any good insight would be highly appreciated not by me but by all on this forum.
Thanks
Thanks
![]() ![]() |
sardar9,
The topic of the CPD-biased exhaust temperature control slope has been covered many many times on control.com, some with "drawings". Use the 'Search' feature at the far right side of the Menu bar at the top of every control.com page.
The thing to remember when looking at the negative slope of the line (curve) is that the line, itself, represents a b>constant firing temperature as CPD varies. So, what the graph tells you is that as CPD increases, exhaust temperature decreases in a combustion turbine.
Yes, it is counter-intuitive, when you consider that as you increase fuel during loading the exhaust temperature increases. But, when holding firing temperature constant as CPD changes.
After you read some of the many threads about that, if you still have questions--ask them here.
The topic of the CPD-biased exhaust temperature control slope has been covered many many times on control.com, some with "drawings". Use the 'Search' feature at the far right side of the Menu bar at the top of every control.com page.
The thing to remember when looking at the negative slope of the line (curve) is that the line, itself, represents a b>constant firing temperature as CPD varies. So, what the graph tells you is that as CPD increases, exhaust temperature decreases in a combustion turbine.
Yes, it is counter-intuitive, when you consider that as you increase fuel during loading the exhaust temperature increases. But, when holding firing temperature constant as CPD changes.
After you read some of the many threads about that, if you still have questions--ask them here.
![]() ![]() |
It provides a higher exhaust temperature at a lower load for more steam production. A higher ttrf1 is also achieved at a lower load thus allowing for greater turndown of the low emissions mode.
It is done by reducing the IGV angle to a lower limit of 42 degrees. A lower air fuel ratio will create a higher ttrf1/ttxm temperature. To prevent compressor surge with the low IGV angles the inlet bleed valve will open. IBH is effectively a compressor recycle valve. IGV angle to IBH flow is a linear relationship. Typically 5% IBH flow at an IGV angle of 42degrees, and decreasing to zero at 57degrees, with some deadband and other compensating factors. IBH may also provide S17 and anti ice protection in some installations.
It is done by reducing the IGV angle to a lower limit of 42 degrees. A lower air fuel ratio will create a higher ttrf1/ttxm temperature. To prevent compressor surge with the low IGV angles the inlet bleed valve will open. IBH is effectively a compressor recycle valve. IGV angle to IBH flow is a linear relationship. Typically 5% IBH flow at an IGV angle of 42degrees, and decreasing to zero at 57degrees, with some deadband and other compensating factors. IBH may also provide S17 and anti ice protection in some installations.
![]() ![]() |
But be careful in what we are saying, Inlet Bleed Heat for DLN control is different from IGV Temperature Control. As CSA indicated IGV Temp control will normally be at an IGV angle of 57-58 Deg. whereas Inlet Bleed Heat for DLN will be at 42 Deg. as 309Guy said
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.
Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.
Fortune
A free society is one where it is safe to be unpopular.
-- Adlai Stevenson

Servo, stepping motor control, analog & web HMI in one system!
Control.com is the largest Automation community on the web. Learn how to advertise here now...








on 24 October, 2012 - 11:44 am
on 24 October, 2012 - 10:35 pm