Dear All;
Our ID fan (110 KW) of Boiler tripped on low water level of steam drum. Again started in auto mode as per logic sequence. however it is observed that direction of rotation is reversed. (Clockwise from original anti-clockwise).
We have stopped ID fan manually & MCCB of VFD were made OFF & then ON. Again started ID fan in manual mode & found direction of rotation in correct manner i.e. anticlockwise.
We haven’t done anything in VFD setting / tampering by any means. What will be the reason for change in direction without changing phase sequence electrically as well as in VFD & any remedial suggestion to avoid such things.