Engineering and workplace issues. topic
Posted by ss on 21 December, 2012 - 6:09 pm
Dear sirs,

Can anybody send or tell me the best way of calculation and calibration of displacer type interface level transmitter.

email:-quadir.abdul77@yahoo.com


Posted by Asok Kumar Hait on 25 December, 2012 - 6:06 am
Hello,

If you want to calibrate a displacer type interface level measuring instrument at field the procedures are simple.

Step-1: Fill up the displacer chamber up to the measurement range (up to the upper nozzle)with lower density fluid and now adjust the transmitter zero to 4 mA.

Step-2: Now fill up the displacer chamber with higher density of fluid and adjust the transmitter span to 20 mA.

That's all! This finishes your calibration. If you don't want to calibrate the transmitter in situ, then you have to take it to the lab and use calculated weight to calibrate the transmitter.

Weight to be calculated considering:
1. When displacer is fully submerged in upper(lower density) fluid and that will give you weight for 4 mA transmitter output;

2. When displacer is fully submerged in lower fluid (higher density fluid)and that will give you weight for 20 mA transmitter output.

Hope this will be of some help to you.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2014 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
"The four building blocks of the universe are fire, water, gravel and
vinyl."
-- Dave Barry
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive