Following diagnostic alarms appeared on running Gas turbine cimplicity screen:
1. Ref-2 voltage out of limit; ID: 167 in PCAA Module of <R> pack.
2. Ref-1 Voltage out of limit ;ID: 168 in PCAA module of <R> pack.
3. Control panel Over temp high
These alarms not getting reset. Checked PCAA module and found ATTN LED RED was blinking.
This time machine was running normally on full load. After 3 hrs, GT goes in shutdown process and following alarms appeared on cimplicity:-
1. Exhaust T/C trouble
2. Combustion control trouble
3. 4 Or More bad change over T/C trouble.
As per logic If 4 Or more bad change over alarm appeared then L94T logic will be true and machine will go in shutdown.
We have started machine again due to crisis of power and again tripped after 3 hrs.
One thing more we have checked all parameters of Exhaust T/C and found only 5 T/C which connected in PCAA<R> Pack increased 80DegF.
PCAA module was replaced with TCAS and alarm normalized.
But i can not get problem route cause why machine will go in shutdown state in MARK-Vie TMR System.
What is calculation of tripping on exhaust T/C?
If any exhaust T/C faulty, then what will impact on machine?
i am completely unknown on exhaust T/C LOGIC. PL explain.
1. Ref-2 voltage out of limit; ID: 167 in PCAA Module of <R> pack.
2. Ref-1 Voltage out of limit ;ID: 168 in PCAA module of <R> pack.
3. Control panel Over temp high
These alarms not getting reset. Checked PCAA module and found ATTN LED RED was blinking.
This time machine was running normally on full load. After 3 hrs, GT goes in shutdown process and following alarms appeared on cimplicity:-
1. Exhaust T/C trouble
2. Combustion control trouble
3. 4 Or More bad change over T/C trouble.
As per logic If 4 Or more bad change over alarm appeared then L94T logic will be true and machine will go in shutdown.
We have started machine again due to crisis of power and again tripped after 3 hrs.
One thing more we have checked all parameters of Exhaust T/C and found only 5 T/C which connected in PCAA<R> Pack increased 80DegF.
PCAA module was replaced with TCAS and alarm normalized.
But i can not get problem route cause why machine will go in shutdown state in MARK-Vie TMR System.
What is calculation of tripping on exhaust T/C?
If any exhaust T/C faulty, then what will impact on machine?
i am completely unknown on exhaust T/C LOGIC. PL explain.