In my site we are facing a problem with gas turbine. The turbine cannot reach “COMPLETE SEQUENCE”. It stops at speed 90% (HP shaft), and the minimum operating speed for complete sequence is set at 95%.
I noticed that on the <I>, when the turbine is at 90%, the active FSR control loop is the START UP control loop. This means, this loop is limiting the fuel gas to the turbine which results in speed limitation to 90%.
I checked this control loop on the CSP, in the BBL, FSRSUPV1 startup FSR and I found the FSR is limited by the parameter FSKSU AR which set as constant at 31.9%.
For your info, the machine is MS5002C (TWO SHAFT MACHINE) which drives centrifugal compressor with Mark5 control system.
I noticed that on the <I>, when the turbine is at 90%, the active FSR control loop is the START UP control loop. This means, this loop is limiting the fuel gas to the turbine which results in speed limitation to 90%.
I checked this control loop on the CSP, in the BBL, FSRSUPV1 startup FSR and I found the FSR is limited by the parameter FSKSU AR which set as constant at 31.9%.