We are currently executing one compressor module project. the suction line size is 30" due the straight length requirement we choose v cone meter for DP measurement where the straight length requirement is less.
- for compensation or mass flow measurement we have added a PT and TT
- The distance of TT from FE is 0.750 meter
- the distance of PT from FE is 7500 meters
- the reason for this the distance we have bend on 30" line followed by a in line strainer
Just want expert comments if there will significant error in the flow reading because of this distance.
I have one option is to use MVT and measure DP and P at the same location and ensure temperature after 7.5 meters.
Please advise
Ayyappan
- for compensation or mass flow measurement we have added a PT and TT
- The distance of TT from FE is 0.750 meter
- the distance of PT from FE is 7500 meters
- the reason for this the distance we have bend on 30" line followed by a in line strainer
Just want expert comments if there will significant error in the flow reading because of this distance.
I have one option is to use MVT and measure DP and P at the same location and ensure temperature after 7.5 meters.
Please advise