Single phasing of 3phase induction motor
Engineering and workplace issues. topic
Posted by jb on 24 February, 2001 - 12:49 pm
Can i still make the motor run near synchronous speed when one of the 3phase lines is disconnected? If so, how? Thanks!


Posted by Steve Snodgrass on 26 February, 2001 - 1:35 pm
You really need all three phases or the motor will run hot(burn up) and fail under load. If you are concerned about loosing a phase while running, then put a VFD (Variable Frequency Drive) on the motor. With this, the drive will continue to supply the motor with 3 phase AC even if you loose an incoming phase or even single phase the drive. As long as the drive's AC/DC Converter sections can supply the DC Bus with enough current to run the motor through the remaining phase(s)it will work. You might have to slightly oversize the drive depending on what you use. To keep the speed synchronous, use a vector drive.


Posted by Johan Bengtsson P&L Automatik AB on 26 February, 2001 - 2:53 pm
If the motor manages to continue to run it will still try to run at the same speed, but it will of course be weaker. If you only have one phase it can't start since it doesn't know the proper direction. /Johan Bengtsson ---------------------------------------- P&L, Innovation in training Box 252, S-281 23 H{ssleholm SWEDEN Tel: +46 451 49 460, Fax: +46 451 89 833 E-mail: johan.bengtsson@pol.se Internet: http://www.pol.se/ ----------------------------------------


1 out of 1 members thought this post was helpful...
Posted by Phil Corso on 26 February, 2001 - 4:46 pm
Post-fault (single-phasing) performance is dependent on pre-fault operating conditions. Please provide some detail so that a meaningful answer can be provided. Regards, Phil Corso, PE Trip-A-Larm Corp (Deerfield Beach, FL)


Posted by R F Redfern on 9 June, 2001 - 7:23 pm
Kind of.You can connect an ac capacitor from one of the other phases to the dead phase of the motor.This produces an artificial phase.
This idea is the basis for commercially manufactured single to three phase converters.
R F Redfern.


Posted by David Brown on 13 June, 2001 - 12:08 pm
But you need a timer to disconect the capacitor
after motor start or your motor will be burnt.


1 out of 1 members thought this post was helpful...
Posted by Phil Corso on 13 June, 2001 - 4:36 pm
Replying to David Brown's Jun13, 11:42 am comment:

Not necessarily! A PTC (Positive Temperature Coefficient) resistor can be used. They are even commercially available to eliminate centrifugal
switch starting of single-phase motors having start-run windings. For those interested look at Murata-Erie products as an example.

Now back to the original problem... loss of one phase. The addition of a capacitor to provide a starting "direction" assumes that the third phase
is available.

Sounds like another case of "catching the mice and letting the elephants go free!"

Regards,
Phil Corso, PE
(Boca Raton, FL)


Posted by David Brown on 14 June, 2001 - 11:11 am
Thank you , I know another different way to use three phase motor in single phase supply but this is only talk, the fact is we should use the right motor to the right supply.
Regards.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2014 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
Wethern's Law:
Assumption is the mother of all screw-ups.
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive