PLCs
Topic: Sensor technologies.
from the maintenance department...
Process Switches NO NC definition
Originally posted by Normally on 19 August, 2011 - 7:12 pm
What "normally" means in process switches.
New Replies:
Dear Sir, Normally means then initial condition of any switch or relay without pressing or...
Topic: PLCs and related questions.
from the Instruments Department department...
Modbus Max. Length
Originally posted by Franco Kew on 8 April, 2014 - 10:34 pm
Measure the total Modbus Length
New Replies:
No that's a star and it's a bad idea because 20 M of unterminated cable will give you reflections...
Dear CWW, Maybe I use the wrong wording in my post, but I am not using the star topology. I try...
Hadn't thought of segmenting the network with repeaters to fix the topology - slick! Franco,...
By Lynn August Linse on 9 April, 2014 - 9:46 am -
This is an RS-485 issue, not Modbus question. Max length is more an issue of the cable quality...
You're not supposed to run RS485 in a star topology. Not sure if short branches are officially...
That doesn't sound like a workable configuration. 485 doesn't like star layouts. You can use...
Topic: Human-Machine Interface and SCADA.
from the Automation List department...
Android tablet for HMI?
Originally posted by Ken E on 3 June, 2011 - 11:18 am
Using an Android tablet as an all in one PLC.
New Replies:
Hello, I found a very good free apps for android and IOs devices (Iphone, Ipad) that is a SCADA...
Gary, I've got a powered USB 4-port hub connected to my Nexus 7. I would think such a device...
You need to connect the power supply lines in the USB connection to a high-current source that can...
Greetings, This subject caught my attention because I working on a project where we are using a...
Originally posted by V K GUPTA on 9 April, 2014 - 12:34 pm
Communication between SIEMENS S7-400 PLC Scalance card to Yokogawa DCS CENTUM CS3000R3
New Replies:
you need to use Siemens CS-3000 module to convert your signal to modbus TCP/IP signal and interface...
By Patrick Lansdorf on 10 April, 2014 - 2:17 am -
Hi, I am guessing that the PLC is a Profibus master... You can use a gateway, such as: ...
Topic: Communications systems and equipment.
from the Forum department...
8-bit data types in Modbus registers
Posted by Jay on 10 April, 2014 - 5:26 am
Are 8-bit data types obsolete for Modbus?
Topic: PLCs and related questions.
from the Forum department...
Flow Rate Calculations S7-1200
Posted by shahien on 10 April, 2014 - 3:40 am
Flow Rate Calculations S7-1200
Topic: PLCs and related questions.
from the Urgent department...
Time and Date in Honeywell control builder
Originally posted by Mostafa on 8 April, 2014 - 2:48 pm
How could use time and date in control module?
New Replies:
Hi Mostafa, you could get the hour, minute and second variables from the CEE under the...
Topic: Continuous process industries, DCS questions.
from the Forum department...
2oo3D voting
Originally posted by amanemisa on 8 April, 2014 - 3:54 am
Explain if 1oo2D voting is just similar to 2oo3 voting for ESD system.
New Replies:
Let's start with your requirement of tripping of valve on rise of line pressure beyond high limit....
Topic: Continuous process industries, DCS questions.
from the HC900-C70R department...
Split Range Control on two valves - HC900-C70R
Originally posted by Frederik on 8 April, 2014 - 7:45 am
Split Range Control on two valves - HC900-C70R
New Replies:
The pressure transmitter is the input to an analog input function block. Its analog value is the...
Topic: Communications systems and equipment.
from the Forum department...
WinConX driver (MBX driver 4.2)
Originally posted by Julio Mtz on 8 April, 2014 - 9:46 am
I need the WinConX driver (MBX driver 4.2) to install an old PCI-85 card
New Replies:
Contact your local Schneider Modicon representative. They might be able to give you a complimentary...
Topic: PLCs and related questions.
from the Over the Cliff department...
Siemens S7 programming
Originally posted by Bapi on 1 April, 2006 - 5:18 pm
Siemens S7 programming
New Replies:
I take issue with this assessment. Take your example of C vs Visual Basic. There's a dramatic...
Topic: Sensor technologies.
from the Instrument department...
ABB Thermocouple Transmitter reading fluctuates
Originally posted by msalem73 on 29 March, 2014 - 6:42 am
Transmitters reading Fluctuating
New Replies:
Okay, You answered some of the questions. Have you checked the thermocouples in the stack to...
first off all i am sorry for writing down transmitter model is ABB TH02. the answer of your...
Hi, I assume the TC's are directly connected to certain thermocouple module. 1-this problem...
msalem73, David asks MANY good questions. But perhaps the best question is: When did this...
check the resistance of the rtd's. you should be able to get a direct reading of the temperature...
1) What is an example of a 'good reading', for example, 215 Deg C? 2) What is an example of a...
Topic: PLCs and related questions.
from the Forum department...
Tri-Sen analog output low
Originally posted by JoeFin on 31 March, 2014 - 6:12 pm
Tri-sen TS 310 controller that doesn't want to output a full 20 ma signal
New Replies:
Possibly a compliance voltage issue? If the load is too light for some reason there isn't enough...
Page 40 of the TS310 User Guide states that the voltage driving the output is 7 volts and that an...
Topic: Sensor technologies.
from the Forum department...
Square root extraction in DCS
Originally posted by oruam on 21 December, 2009 - 6:35 am
Square root extraction in DCS
New Replies:
By hemantkumar chauhan on 31 March, 2014 - 9:44 am -
Okay I am not your ones right or not.. but I have my own .. Let me explain it.. ...
Topic: Communications systems and equipment.
from the Forum department...
Modifying a timer - SLC 504
Originally posted by Don Leathers on 28 March, 2014 - 4:29 pm
Having an issue finding where a source comes from in a MOV command.
New Replies:
> Does the PLC have a memory module installed? > If it does, you will have to save the...
Since you have no programming that changes the value of register N21, it seems likely that there is...
Does the PLC have a memory module installed? If it does, you will have to save the change to the...
Topic: PLCs and related questions.
from the Senior Controls Engineer department...
IDEC PLCs
Posted by J. Parrish on 30 March, 2014 - 4:51 pm
Forum reader is pro-IDEC PLCs. Training session in Houston in April
Posted by Cleto on 27 March, 2014 - 10:42 pm
Equivalent register address of PLC to SCADA
Topic: PLCs and related questions.
from the Automation List department...
Comparing PLC and DCS
Originally posted by Anonymous on 6 May, 2004 - 6:34 pm
I am new in the field of automation. Could anybody tell me the difference between PLC and DCS other than I/O handling capacity?
New Replies:
People are still giving answers because many users still don't know the differences between a PLC...
Posted by Sara on 27 March, 2014 - 12:03 pm
Please read the text for full information. The attack codes I am talking about are for DoS and Injection attacks.
Topic: Sensor technologies.
from the I&C department...
ATEX Ex ic or ATEX Ex nA ?
Originally posted by Daniel on 12 March, 2014 - 11:21 pm
ATEX Ex ic or ATEX Ex nA ?
New Replies:
Hi, Normally from technical point of view it is required unification of solution. So if you use...
Topic: PLCs and related questions.
from the Automation List department...
So What did I use the Clicks for?
Originally posted by Curt Wuollet on 22 March, 2014 - 8:37 pm
Real world example of using the Koyo Click PLC
New Replies:
> Don't really care for the Clicks (although ADC's new Do-More PLC is a > fantastic product...
Don't really care for the Clicks (although ADC's new Do-More PLC is a fantastic product except for...
Topic: Communications systems and equipment.
from the Forum department...
File Handling through Micro Controller
Originally posted by Prem Sanil on 25 March, 2014 - 8:25 am
Using Micro Controller to do file handling on a PC
New Replies:
> Presently able to do communication with Hyper Terminal (Micro Controller > connected to PC...
ya i know through Linux is less complicated to achieve this, but my Application needs to do this...
Select Page: Previous 5 6 7 8 9 10 11 12 13 14 15 Next
 
 

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2014 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
Everything should be built top-down, except the first time.
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive