Why does a core (say for ex of a transformer/or an alternator) saturate?
We have in our gas turbine frame 7E a problem of failure to start due to starting clutch disengage.
Fuel and Load Hunting after Full speed and massive with generator breaker closed
New Replies:
> And i Forgot to say that the unit is working on Ovation system by Emerson
Is the Ovation...
Ahmad,
One other very common cause of instability and hunting is liquid fuel supply pressure....
Ahmad,
I don't think you're going to find much experience here with Ovation control systems on...
And i Forgot to say that the unit is working on Ovation system by Emerson...
Looking for information on Siemens V94.2 Gas Turbine Exhaust Temperature Measurement
what are you to do when outgoing line breaker trips
New Replies:
By sb on 22 April, 2013 - 3:57 am -
Dear Stephen
Mention the details how many outgoing lines do you have and what is busbar scheme...
Is HP bypass flow necessary to control power plant?
New Replies:
By sb on 22 April, 2013 - 3:49 am -
Bypass system is generally used in Combined Cycle Power Plants.
Purpose of keeping HP bypass OPEN...
By Pavalavannan.B on 13 April, 2013 - 5:24 am -
Hi,
It is not necessary to measure flow of HP B/P because Pressure is the one to be controlled....
When we try to put the machine to turning we get the following trip "Starting means turbine shaft fail to break turbine away"
New Replies:
By sb on 22 April, 2013 - 3:29 am -
Very interesting topic..
I have got many points from experience you shared. We do have suffered...
By tony salman on 20 April, 2013 - 8:30 am -
Dear All
i read all experience share that is good notes. but i think the problem get from lube...
By Chandra on 13 April, 2013 - 12:27 pm -
We are using 6 Units Frame 9E gas turbines and we often have the problem with failure to break...
Iron in IP Boiler
New Replies:
By d- on 20 April, 2013 - 10:13 am -
the non-volatile components will be concentrated,
blowing down the boiler is about the only way...
Dkguerry.... can you provide a unit-of-measure, i.e., grains per gallon, or mg per liter?
...
G771 Moog servovalve and a G123-825 buffer amplifier for a gas turbine.
Would you say that testing of interposing relays is important outside of the nuclear industry?
New Replies:
By Bob Peterson on 19 April, 2013 - 2:49 pm -
another thought. it may well be cheaper to just replace these kind of relays as opposed to trying...
Diffuser leakage
New Replies:
Searching,
Yes. Heat causes expansion, and expansion of a bearing housing can cause alignment...
Procedure for selection of gas turbine and steam turbine for a combined cycle power plant.
New Replies:
Suman,
The only question we can possibly answer based on the information provided is the one...
How to bring GT from Base load to Full speed no load manually??
New Replies:
sriram sandeep,
It would be done exactly as you describe. Unload the machine (manually or...
Why we need to kept GCB as a synchronisation breaker for gas turbine instead of using the line breaker as like steam turbine..
New Replies:
sriram sandeep,
Some sites synchronize the gas turbine generator across a breaker that is on the...
hydrogen cooling system for GE frame6 generator manual
New Replies:
By naransinh on 19 April, 2013 - 1:17 am -
the information helped me a lot to understand this system. thank you so much. but i still have one...
Cyber Security training for Power Generation Professionals, May 17th outside of Chicago.
GasBooster compressors could not be started after a sudden dip in grid. Thrust pads of High speed shaft in gear box completely damaged. Compressor bearings found no damage. Is there any chances of Antisurge valve malfunctioning?
Mk6b control status. status is showing minor difference.
New Replies:
Eskay,
Funny you should post this question today, as I have spent several hours by telephone and...
I would like to add the MK-5 Date and Time to a historian.
New Replies:
By curiousone on 17 April, 2013 - 7:44 pm -
Actually it is much easier to ensure that the HMI, MKV, and the historian are synchronized to a...
please share your views on the MV Drives business in India,
I am doing a market research report for India...
I am doing a market research report for India...
New Replies:
Hi NKS,
India is always a Growth Region market having huge potential for MV AC Drives.
...
We would like share the experience for GPRS application.
New Replies:
By DR Sharma on 16 April, 2013 - 6:31 am -
I am interested to transmit my real time generation data to state load dispatch center through...
from the Instrumentation and control department...
Back Pressure Control Mode In Toshiba steam turbine D-EHC control systemWhat is the Back pressure mode in Toshiba steam turbine ?and what is the running condition for this mode?
What will happen when 2 out of 3 poles of a 220 kv circuit breaker of a 330MVA Generator (of a steam power plant) is closed and one open when the generator (via GT) is connected (or synchronized)with 220kv bus?
New Replies:
Santanu... The disturbance question I replied to was just the opposite of what you described, and I...
Santanu... if closure of the faulted-breaker at the instant both the generator-side PTs and the...
Santanu Das,
The answer to this is complicated to explain in words. The simple, but not...
Mark VIe PDIO cards failing very frequently. We are looking for a company to conduct an RCA on the failures and provide corrective actions to minimize/eliminate failures.
We are derating a 22kV YSF6 panel to 11kV. We need 2 x 11kV/110V SQRT3, 3p, class 0.5 50VA busbar mounted VTs.
Anyone know we can get some
Anyone know we can get some
how to calculate the power in MW that drives the compressor...
New Replies:
By Brian Freeman on 12 April, 2013 - 9:10 pm -
from what I understand...
MW = (J/s)*3600(s/hr)=3600(J/hr)=>MWhr=3600J
Lets say MWhr/kg...
Behavior of a power plant when its load rate (stag ms9001fa) drops.
New Replies:
GE sets the loading rates so as to maximize the operating life of the equipment. Or, perhaps, so as...
The lube oil filter on GE Frame 9FA machines only works when we are opening the 1/2" Filter drain valve.
New Replies:
Ashutosh,
You also have a P&ID of the lube oil system, which you can use to understand how...
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.
Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.
Fortune
One of the lessons of history is that nothing is often a good thing to
do and always a clever thing to say.
-- Will Durant