Dear WTF,
thanks a lot
- Has the ambient temperature (the temperature of the air entering the axial compressor changed from when the shutdown was working correctly until now? / No
- How long has it been since the last maintenance inspection was completed? Immediately prior to this flameout problem starting? Or weeks or months prior? / Months
- if the machine is a dual fuel / light crude oil & distillate
- clearly if exhaust temperature spreads increased recently, especially during shutdown / we will see
- at the time of trip by loss of flame LCO FWRD pump pressure was 6.1 bar and VC3-1 opening was 5%
- at the time of trip by loss of flame liquid fuel pump disch. pressure was 9.4 bar
- at the time of trip by loss of flame VS1-1 was opened
thanks a lot