We have a 25 mw extraction cum condensing turbines and we have a low load limiter which comes in picture when machine is on speed control (droop control) otherwise same is deactivated when we are on load control.
This low load limiter is interfering with speed control and is brining down the mw generation to it's limit, i.e. 3 mw and this is happening whenever we change from load control to speed control.
The output of speed/load control & load limiter are connected to a MIN selector block and whichever control is having the lower output controls the machine.
This low load limiter is interfering with speed control and is brining down the mw generation to it's limit, i.e. 3 mw and this is happening whenever we change from load control to speed control.
The output of speed/load control & load limiter are connected to a MIN selector block and whichever control is having the lower output controls the machine.