Potential free contacts are contacts which do not have a voltage potential on them. Ie, if a device must be connected to potential free contacts, then no other circuit or device may be connected to the same contacts.
Potential free contact as name suggest a contact established without any potential into it. This is also called some times as dry contact. Relays also provide p.f. contact. When the relay is energised, there is no potential in P, NO, or NC. But change over takes place.
Potential free contacts are also sometimes called volt free or "dry" contacts, and simply refer to relay contacts, or switch or sensor contacts, which haven't been wetted with voltage by the machine or device in which they exist. It doesn't refer to some characteristic of the contacts themselves.
So if you were interfacing to a machine with dry contact outputs for interlocks, you would have to provide the circuit voltage source as well as
the relay coil or PLC input or other means of accepting and utilizing the information represented by the contact.
Steve Myres, PE
Automation Solutions
(480) 813-1145
To me a relay is a potential free contact because the relay terminals are isolated from the electronics of the device. This contrasts e.g. to
transistors and triacs that are not potential free contacts because they are connected to controlling electronics.
Hello Rajini,
It means, the contacts has no potential connected from the device they are in, eg. when you got potential free relay output in PLC, you can connect one connector's side to external supply and the second one to your load (eg. coil).
Piotr Kowalski
Potential free contacts are volt free contacts. In selecting a PLC or DCS input module you may ask vendor for potential free contacts. The potential free contacts are used in applications where intrinsically safe electrical classification is required. Potential free contacts are used as a safety in hazardous area where a sparks may ignit the combustible atmosphere.
it is same like switch, which contacts are made or brake by magnetic coil. that coil is powered by or connected to controlling circuit normally PCBs. But contacts are use for other external devices. you can checked with multimeter in that contacts make or brake (continuity, such as ohm). making or breaking is useful for other external devices, in which current or voltage pass through it. In short, making or breaking is control by controlling circuit, while contacts are connected to other external devices. they are call potential free contacts where you cannot measure voltage if external device is not connected to it.
In interfacing PLCs with external systems (eg Dcs or mcc) the FVC or potential free contacts are used in case the reading system will wet the contact to read it (which is common case).
We published an article a while back comparing wet and dry contacts, which is essentially the same concept as contacts with or without potential (voltage) applied.
You can check that out here, and I hope it helps if you visit this thread and need more information!
