Regards,
Phil Corso, PE
If their X to R ratios are equal, then of course their percent impedances are equal, making the equations simpler! If any or all of the 3-factors are different a circulating current will exist between the two transformers, even at no-load!
Regards, Phil Corso, PE (cepsicon@aol.com
So can I understand that even if the X/R is different the XTR can opetate parallel if the %impedance is same with the same vector group and turns ratio,preventing circulating current.
Regards
1) A circulating current exists if they have equal pct impedances but different X/R ratios!
2) A circulating current exists if they have equal X/R ratios, but different pct impedances!
For either case you must calculate the level of circulating current to determine its impact on safe operation!
Regards, Phil Corso (cepsicon@aol.com)
a) Consider two transformers, A and B, having equal capacity, voltage-ratio, and percent-impedance! They will each carry 50% of the load, and circulating-current is virtually zero!
b) If A’s impedance is twice that of B, say 6% vs 3%, respectively, then A will carry 2/3 of the load, while B carries 1/3. In other words, if two 1,000-kVA transformers are supplying a 1,800-kVA load the one with the 6% impedance will carry 600-kVA and the other 1,200-kVA!
c) The case when the impedances are equal but X/R ratios are different doesn't yield a simple “word-description” that will adequately express the outcome!
d) Addressing your question about different voltage-ratios, regardless of impedances and/or X/R ratios differences: consider transformer A with a 400-V as its secondary no-load voltage, while B’s is 415-V; further, let Za and Zb represent the impedances (in ohms) of transformer A and B, respectively. Then the circulating current, equals,
Ic = [Vb (higher secondary voltage) – Va (the lower secondary voltage] / [Za + Zb], Amps
In conclusion, for the condition when voltage-ratios are equal, but the impedance and/or X/R ratios are different, then the load carried by one transformer is proportional to the other’s impedance divided by the sum of both impedances. Hence, the distribution is fairly easy to establish. On the other hand, circulating-current is much more difficult to determine! For the simple case when voltage-ratios are different, the formula in part d) can be applied! But, popularizing the famous song… “Don’ worry”… because manufacturers build to standards that try to limit resistance and reactance variations. Thus, it is unlikely (but, still possible) that circulating-currents will exist! So, when in doubt… run the numbers!
Regards, Phil Corso (cepsicon@aol.com)
Regards,
Lee, Hyonwoo
There are three distinct currents: two are the transformer secondary load-currents, Ia and Ib, respectively; and the third, Ic, representing the circulating-current! The latter results from parameter asymmetries noted in earlier posts. And, because the subject becomes more difficult for three-phase transformers, I will discuss single-phase transformers. Also, please note, that when sums of components are involved, they must be added vectorially, and not arithmetically:
1) Supply current, I�a + I�b, (Ia + Ib, adjusted for voltage-ratio.)
2) Primary-winding currents, I�a and I�b, respectively (Ia + Ib, adjusted for voltage-ratio.)
3) Secondary-winding currents, Ia + Ic, and Ib - Ic, respectively.
4) Load current, Ia + Ib.
I realize that verbal description is difficult, so if you have a specific case in mind, contact me on or off List!
Regards, Phil Corso
I have 2 transformers in parallel. One 12/20 MVA 67/4.16kV, Z=7.29% and another 7.5/9.375MVA 70/4.360kV (because of how the taps are set) and Z=7.88%.
Thanks,
Mani
Unfortunately, it not only contains Vector-Algebra, but Complex-Number notation as well, so the mathematically-impaired need not apply!
Regards,
Phil Corso (cepsicon@aol.com)
Krishna, turns-ratio and voltage-ratio are different parameters. You must use voltage-ratio, that is, the primary phase-to-phase voltage divided by the secondary phase-to-phase voltage!
Regards, Phil Corso (cepsicon@aol.com)
Regards, Phil Corso (Cepsicon@aol.com)
Phil Corso
can i make this two transformers parallel?will there be significant circulating currents which will damage the transformers in long term? at the moment these two transformers supply separate loads which are unequal and the highest load so far is 580kVA from one transformer and 450kVA from the other transformer.. on average the total load is around 500 - 600kVA. Please help me phill.thanks for the above posts.
Regards, Phil Corso (cepsicon@aol.com)
1) The transformer with the lower impedance will carry 51% of any combined load, to 1,200-kVA!
2) The other will carry 49%!
3) Circulating current is nil!
My earlier offer to Mani applies to your situation as well.
Regards, Phil Corso (cepsicon@aol.com
- ABCs of SBCs: Single board computers for embedded control; Lego learning
- Less, more: NEMA cites less confidence; NAM sees more exports of manufactured goods
- Free webinar on Zigbee for embedded systems
- Better together? Ametek, Dresser-Rand, IntervalZero, Rexroth make acquisitions
- You need 2 monitors: This Website will prove it
- Preview: Mitsubishi iQ controls sequence, motion, process, CNC, robotics; has connectivity
- 30 new Rockwell Automation products integrate hardware, software
- Digital manufacturing: Autodesk Inventor shows component interactions
- Software certified by AT&T: Runs on PDAs, cellphones, enables mobile applications
- Research: HMI supervisory software use increases with service needs
Patronize our advertisers!