from the Hazardous classification department...
Hazardous ClassificationPlease give the details about the difference between materials for EExe and EExd.
What makes the significance of EExe and EExd materials usage?
Thanks & regards.
What makes the significance of EExe and EExd materials usage?
Thanks & regards.
Hi Bharat,
The difference between Ex d and E e is that any Ex d equipment must be able to withstand an internal explosion of the flammable material without the flame propagating to the atmosphere to the outside, while Ex e equipment does not permit any sources of ignition inside the equipment and flame propagation is not an issue.
Ex d equipment is robust enough not to deform or be otherwise affected by an internal explosion. Accordingly, it usually uses thick metal castings. Ex e equipment is designed only to maintain the required Ingress Protection level of IP54 or better and can be made from any material (metal or plastic) that is suitable for the service. Ex e equipment does not require the large amounts of material that are needed for Ex d.
Both must be selected taking into account issues such as external corrosion agents, effects of UV exposure, or other factors that could act to reduce the integrity of the equipment.
Hope this helps,
Bruce
The difference between Ex d and E e is that any Ex d equipment must be able to withstand an internal explosion of the flammable material without the flame propagating to the atmosphere to the outside, while Ex e equipment does not permit any sources of ignition inside the equipment and flame propagation is not an issue.
Ex d equipment is robust enough not to deform or be otherwise affected by an internal explosion. Accordingly, it usually uses thick metal castings. Ex e equipment is designed only to maintain the required Ingress Protection level of IP54 or better and can be made from any material (metal or plastic) that is suitable for the service. Ex e equipment does not require the large amounts of material that are needed for Ex d.
Both must be selected taking into account issues such as external corrosion agents, effects of UV exposure, or other factors that could act to reduce the integrity of the equipment.
Hope this helps,
Bruce
Futher to add to Bruce
In Ex e (Increased Safety) type of protection, measures are applied to prevent possibility of arc or sparks or excessive temperature inside electric equipments (mostly motors, electrical fittings come with Ex e certification) Further Ex e equipments are permitted to be used in T1,T2 and T3 class only.
Ex e do not permit arc or spark to occur.
While Ex d on the other hand, allow spark or arc to happen, but do not allow for propagation of flame to potentially explosive atmosphere.
Regards
C Potdar
In Ex e (Increased Safety) type of protection, measures are applied to prevent possibility of arc or sparks or excessive temperature inside electric equipments (mostly motors, electrical fittings come with Ex e certification) Further Ex e equipments are permitted to be used in T1,T2 and T3 class only.
Ex e do not permit arc or spark to occur.
While Ex d on the other hand, allow spark or arc to happen, but do not allow for propagation of flame to potentially explosive atmosphere.
Regards
C Potdar
Hi C Potdar,
You state that Ex e equipment is permitted to be used in T, T2 and T3 class only. Can you give me a reference to any IEC standards relating to this as I have never come across this restriction - or is it a local requirement for
your area only?
Cheers,
Bruce.
You state that Ex e equipment is permitted to be used in T, T2 and T3 class only. Can you give me a reference to any IEC standards relating to this as I have never come across this restriction - or is it a local requirement for
your area only?
Cheers,
Bruce.
From Control Engineering magazine...
Related articles from Control Engineering magazine- Integrating PLM, ERP, MES behind the scenes
- Enterprise data historian supports management of power distribution
- Digital factory interface: XML control logic standard accepted by AutomationML
- Colfax Corp. acquires Fairmount Automation
- Oil & gas industry controller benefits from embedded database
- Wonderware names InSource “Wonderware Southeast” partner
- Researcher wins grant for holographic instrument panel controls
- Rittal launches Ri4Power power management system
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.
Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.
Our Advertisers
Help keep our servers running...
Patronize our advertisers!
Patronize our advertisers!