While setting up communication between Yokogawa Centum CS300 and Bently 3500/92 Comm gateway module, i am not able to get correct values of the analog data from holding resisters. Whereas the status data (digital), i.e, alarm or trip states are received without any issues.
Communication settings in the slave i.e 3500/92 are as below,
Full Scale Data Range: 4095
Baud Rate: 9600
Parity: Even
Stop Bits: One
Byte Timeout: 3 Byte
Numeric Format: Hexadecimal
Word Swapped: Enabled
What could possibly be the error on the Yokogawa settings? For redundancy purposes, Two parallel serial links of RS485 are used with two slave devices on each link. Slave addresses are kept identical on both the links i.e 1&2.
Appreciate a quick response.