Hi,
I have a process of 3 closed-loop pressure loops that slowly (30 min or so) oscillate 4% around setpoint 100% of the time. I have been trying to tune these loops for the past week using ExperTune software but since I lack experience with the software and tuning in general, I have found it to be less than helpful. I have been reading about the different types of loops and was hoping to get some thoughts from the group.
The series of loops in order are: Boiler->Header->Steambox. The boiler and header loops are always running and have fixed set points of 125 and 30 PSIG respectively. The header feeds multiple processes but only the steambox valve is oscillating with the header. The steambox setpoint changes depending on the product we run but stays fixed throughout the run (for reference, it's around 15 PSIG).
At this point, I have confused myself on how I should be tuning these loops. If I've interpreted what I've read correctly, I need to detune the loops so that they are not controlling at the same period. I believe I should be tuning the boiler loop to be the fastest and the steambox to be slowest but my intuition is telling me that it should be the other way around. That is to say, I'd want the steambox to be the fastest because that is what I'm controlling for my end process and therein lies my confusion.
I had actually gone the way of making the header and steambox feedforward loops and feeding the upstream of each into the downstream but I think I misunderstood the purpose and I havent been able to make it work like expected.
Any advice to the situation would be helpful. Thank you.
I have a process of 3 closed-loop pressure loops that slowly (30 min or so) oscillate 4% around setpoint 100% of the time. I have been trying to tune these loops for the past week using ExperTune software but since I lack experience with the software and tuning in general, I have found it to be less than helpful. I have been reading about the different types of loops and was hoping to get some thoughts from the group.
The series of loops in order are: Boiler->Header->Steambox. The boiler and header loops are always running and have fixed set points of 125 and 30 PSIG respectively. The header feeds multiple processes but only the steambox valve is oscillating with the header. The steambox setpoint changes depending on the product we run but stays fixed throughout the run (for reference, it's around 15 PSIG).
At this point, I have confused myself on how I should be tuning these loops. If I've interpreted what I've read correctly, I need to detune the loops so that they are not controlling at the same period. I believe I should be tuning the boiler loop to be the fastest and the steambox to be slowest but my intuition is telling me that it should be the other way around. That is to say, I'd want the steambox to be the fastest because that is what I'm controlling for my end process and therein lies my confusion.
I had actually gone the way of making the header and steambox feedforward loops and feeding the upstream of each into the downstream but I think I misunderstood the purpose and I havent been able to make it work like expected.
Any advice to the situation would be helpful. Thank you.